(This is a question mostly for North American users, I realize in EU you have fancy 220v)
With black Friday sales on-going, I figure I might pick up a ups for incoming H3C. Do I need something that can support a 20A input? How close does H3C get to maxing out the regular 15A outlet with bed + chamber heating?
I am going to have electrician install a dedicated 20A line for the printer / office soon as well.
Do you plan to buy a “UPS” or get something like a Jackery system which provides a UPS feature?
I have a rather decent size system with zero millisecond UPS functionality that I need to haul downstairs.
Anyways, if you plan to have a dedicated 20A circuit then you might as well buy a unit that can also offer a 20A UPS circuit on the ouput. Specs claim a maximum of 1850 watts on the 110-120V configuration, or a maximum current of 16.8 amps at 110v.
The reason I decided to get 20A line is because there will be other stuff connected simultaneously and I don’t want to have to worry about blowing a fuse when printer starts while other things (laptop, air purifier, maybe additional filament dryer) are running already
A 2200 VA (1980w output) UPS is around $400 and has an 8 minute run time.
Or, you can spend $1500 and extend that runtime with a lead battery that weighs a ton and it still can’t provide a 30 minute run time. Prices from there just keep going up.
A pecron F3000 LFP for example has a 3,000 watt rated output, costs $900, and will run a 2000 watt load for well over an hour (3kwh capacity).
The major difference is the reliability of the “solar generator” systems will not be as industrial grade as a UPS of similar specifications, however it would handle the 2kw load with ease. Also, depending on the type and quality of the UPS vs the “solar generator” system there may be some additional power overhead. Some of them require the inverter be powered on at all times to provide UPS functionality and I dont know how that relates to a “real” UPS.
My Pecron unit (F5000 LFP) has a nearly constant 52 watt power draw, but it’s also got a 7200w inverter so that’s the trade I make. I use it as a home backup though, but I figure I will put the printer on it as a nice-to-have.
A single 20a line at 110v will provide a maximum continuous rated (>3 hrs, 80% of max) current of just 1760w. 1920w @ 120v. 2200/2400 peak load (under 3 hours) is considered acceptable.
That said, the printer should not require such huge power constantly and your described situation should fall well into peak usage. This would mean you need a UPS/power solution capable of delivering up to 2400 watts if you have the coin to spend.
If you want to save a little and solely use it for the printer than a ~1900w continuously rated system would suffice.
The kind of powerful UPS you need for H series printers is usually very poor value
Consider getting a Power Station instead. Many even function as UPS. You’ll get easily 2x the capacity and power just by searching for that phrase instead of UPS. My personal favorite is Pecron, but admittedly the more mainstream ones have better specific UPS-cutover features.
Printers use a lot of resistive heating for long periods of time so look at the continuous power rating, not the “max surge” advertisement slop. When they talk about surge, they mean motor inrush like starting a table saw - which is done in a second - the “large spikes” of a chamber heater last for minutes, it is not the kind of surge they are talking about.
Is the consideration for a UPS based on the stability of the power grid, or to prevent a circuit breaker to be triggered?
Afaik there is a Power reduction mode on the H3C that should not trigger a circuit breaker.
Maybe we are lucky in the Netherlands, but here the power grid is highly reliable, offering around 99.99% to 99.995% security of supply.
So investing in a UPS for that is here a waste of money.